How can resolve problem A2008 PANEL LOSS Alarm in ABB ACS550 Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Panel communication is lost and either:
Drive is in local control mode (the control panel displays LOC), or
Drive is in remote control mode (REM) and is parameterized to
accept start/stop, direction or reference from the control panel.
To correct check:
Communication lines and connections.
Parameter 3002 PANEL COMM ERR.
Parameters in Group 10: START/STOP/DIR and Group 11:
REFERENCE SELECT (if drive operation is REM)