Forum

Share:
Notifications
Clear all

A2008 PANEL LOSS Alarm in ABB ACS550 Drive

2 Posts
1 Users
0 Reactions
496 Views
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem A2008 PANEL LOSS Alarm in ABB ACS550 Drive ?

1 Reply
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Panel communication is lost and either:
• Drive is in local control mode (the control panel displays LOC), or
• Drive is in remote control mode (REM) and is parameterized to
accept start/stop, direction or reference from the control panel.
To correct check:
• Communication lines and connections.
• Parameter 3002 PANEL COMM ERR.
• Parameters in Group 10: START/STOP/DIR and Group 11:
REFERENCE SELECT (if drive operation is REM)

Reply
Share: