How can resolve problem A2024 ENCODER ERROR Alarm in ABB ACS550 Drive ?
The drive is not detecting a valid encoder signal. Check for and
correct:
Encoder presence and proper connection (reverse wired, loose
connection or short circuit).
Voltage logic levels are outside of the specified range.
A working and properly connected Pulse Encoder Interface Module,
OTAC-01.
Wrong value entered in parameter 5001 PULSE NR. A wrong value
will only be detected if the error is such that the calculated slip is
greater than 4 times the rated slip of the motor.
Encoder is not being used, but parameter 5002 ENCODER ENABLE =
1 (ENABLE).