How can resolve problem F0002 or F 2 DC OVERVOLT Fault in ABB ACS550 Drive ?
1 Reply
Dec 14, 2021 12:29 pm
Intermediate circuit DC voltage is excessive. Check for and correct:
• Static or transient overvoltages in the input power supply.
• Insufficient deceleration time (parameters 2203 DECELER TIME 1 and
2206 DECELER TIME 2).
• Undersized brake chopper (if present).
• Verify that overvoltage controller is ON (using parameter 2005).