ABB ACS550 Drive
1
Posts
1
Users
0
Reactions
245
Views
Jun 21, 2024 5:55 am
Cause : AI 2 LOSS comes when the analog input 2 signal has been lost or is not within the expected range. This fault typically occurs when the drive is configured to receive a signal on AI2 and the signal is missing or outside the predefined limits.
Check for and correct:
- Source and connection for analog input.
- Parameter settings for AI2 FAULT LIMIT (3022) and 3001 AI< MIN FUNCTION .