Forum

Share:
Notifications
Clear all

F0024 OVERSPEED Fault in ABB ACS550 Drive

2 Posts
1 Users
0 Reactions
5,305 Views
Posts: 19708
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem F0024 OVERSPEED Fault in ABB ACS550 Drive ?

1 Reply
Posts: 19708
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Motor speed is greater than 120% of the larger (in magnitude) of 2001
MINIMUM SPEED or 2002 MAXIMUM SPEED. Check for and correct:
Parameter settings for 2001 and 2002.
Adequacy of motor braking torque.
Applicability of torque control.
Brake chopper and resistor.