F1005 PAR PCU 2 Fault in ABB ACS550 Drive

2 Posts
1 Users
0 Reactions
4,190 Views
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem F1005 PAR PCU 2 Fault in ABB ACS550 Drive ?

1 Reply
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Parameter values for power control are inconsistent: Improper motor
nominal kVA or motor nominal power. Check for the following:
1.1 < (9906 MOTOR NOM CURR · 9905 MOTOR NOM VOLT · 1.73 / PN) < 3.0
where: PN = 1000 · 9909 MOTOR NOM POWER (if units are kW)
or PN = 746 · 9909 MOTOR NOM POWER (if units are hp, e.g. in US)

Reply