How can resolve problem F1005 PAR PCU 2 Fault in ABB ACS550 Drive ?
1 Reply
Dec 15, 2021 11:32 am
Parameter values for power control are inconsistent: Improper motor
nominal kVA or motor nominal power. Check for the following:
• 1.1 < (9906 MOTOR NOM CURR · 9905 MOTOR NOM VOLT · 1.73 / PN) < 3.0
where: PN = 1000 · 9909 MOTOR NOM POWER (if units are kW)
or PN = 746 · 9909 MOTOR NOM POWER (if units are hp, e.g. in US)