How can resolve problem F1013 PAR PFC IO 2 Fault in ABB ACS550 Drive ?
1 Reply
Dec 15, 2021 11:38 am
IO configuration is not complete – the actual number of PFC motors
(parameter 8127, MOTORS) does not match the PFC motors in Group 14:
RELAY OUTPUTS and parameter 8118 AUTOCHNG INTERV.