How can resolve problem F1016 PAR USER LOAD C Fault in ABB ACS550 Drive ?
1 Reply
Dec 15, 2021 11:40 am
Parameter values for the user load curve are inconsistent. Check that the
following conditions are met:
• 3704 LOAD FREQ 1 < 3707 LOAD FREQ 2 < 3710 LOAD FREQ 3 <
3713 LOAD FREQ 4 < 3716 LOAD FREQ 5.
• 3705 LOAD TORQ LOW 1 < 3706 LOAD TORQ HIGH 1.
• 3708 LOAD TORQ LOW 2 < 3709 LOAD TORQ HIGH 2.
• 3711 LOAD TORQ LOW 3 < 3712 LOAD TORQ HIGH 3.
• 3714 LOAD TORQ LOW 4 < 3715 LOAD TORQ HIGH 4.
• 3717 LOAD TORQ LOW 5 < 3718 LOAD TORQ HIGH 5