How can resolve problem 7183 BR excess temperature Fault in ABB ACS560 Drive ?

1 Reply
Posts: 14958
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Brake resistor temperature has exceeded fault limit defined by parameter 43.11 Brake resistor fault limit.

1. Stop drive. Let resistor cool down.
2. Check resistor overload protection function settings (parameter group 43 Brake chopper).
3. Check fault limit setting, parameter 43.11 Brake resistor fault limit.
4. Check that braking cycle meets allowed limits.