ABB ACS560 Drive
2
Posts
1
Users
0
Reactions
3,186
Views
Jul 14, 2021 12:41 pm
How can resolve problem 8009 Current limit fault in ABB ACS560 Drive ?
1 Reply
Jul 14, 2021 12:42 pm
Cause : Motor actual current exceeded the limit defined in parameter 30.17 Maximum current.
1. Reduce the motor load.
2. Check for any jam or stall in motor.
See parameter 30.17 - Maximum current.