Forum

Share:
Notifications
Clear all

A491 External temperature alarm/warning in ABB ACS560 Drive

2 Posts
1 Users
0 Reactions
1,032 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem A491 External temperature alarm/warning in ABB ACS560 Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Measured temperature 1 or 2 has exceeded warning limit.

1. Check the values of parameters

35.02 - Measured temperature 1 and

35.03 - Measured temperature 2.

2. Check the cooling of the motor (or other equipment whose temperature is being measured).

3. Check the warning limits for measured temperatures 1 and 2 in parameter group 35 Motor thermal protection.

Reply
Share: