How can resolve problem A582 Auxiliary fan missing alarm/warning in ABB ACS560 Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : An auxiliary cooling fan (IP55 internal fan) is stuck or disconnected.

1. Check the auxiliary code.
2. Check the auxiliary fan and connection.
3. Replace faulty fan.
4. Make sure the front cover of the drive is in place and tightened.

If the commissioning of the drive requires that the cover is off, this warning will be
generated even if the corresponding fault is defeated.