Forum

Share:
Notifications
Clear all

A6A7 System time not set alarm/warning in ABB ACS560 Drive

2 Posts
1 Users
0 Reactions
542 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem A6A7 System time not set alarm/warning in ABB ACS560 Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : System time is not set. Timed functions cannot be used and fault log dates are not correct.

1. Set the system time manually or connect the panel to the drive to synchronize the clock.

2. If basic panel is used, synchronize the clock through the EFB or a fieldbus module.

3. Set parameter 34.10 Timed functions enable to Disabled to disable the timed functions if they are not used.

Reply
Share: