How can resolve problem A6E5 AI parametrization alarm/warning in ABB ACS560 Drive ?
1 Reply
Jul 13, 2021 9:58 am
Cause : The current/voltage jumper setting of an analog input does not correspond to parameter settings.
1. Adjust either the jumper setting (on the drive control unit) or parameter
12.15/12.25.
Note: Control board reboot (either by cycling the power or through parameter 96.08 - Control board boot) is required to validate any changes in the jumper settings.