A794 BR data alarm/warning in ABB ACS560 Drive

2 Posts
1 Users
0 Reactions
590 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem A794 BR data alarm/warning in ABB ACS560 Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Brake resistor data has not been given.

1. One or more of the resistor data settings (parameters 43.08…43.10) is incorrect.
The parameter is specified by the auxiliary code

0000 0001   Resistance value too low.                          Check value of 43.10.

0000 0002   Thermal time constant not given.              Check value of 43.08

0000 0003   Maximum continuous power not given.      Check value of 43.09.

Reply