How can resolve problem A7AB Extension I/O configuration failure alarm/warning in ABB ACS560 Drive ?
1 Reply
Jul 13, 2021 12:09 pm
Cause : Installed C-type module is not the same as configured or the communication between the drive and module has been disturbed.
1. Check that the installed module
(shown by parameter 15.02 Detected extension module) is the same as selected by parameter 15.01 Extension module type.
Eliminate the disturbance sources.