ABB ACS560 Drive
428
Jun 15, 2024 12:20 pm
Cause : FBA A communication comes when cyclical communication between drive and fieldbus adapter module A or between PLC and fieldbus adapter module A is lost.
The A7C1 warning in your ABB ACS560 drive indicates a communication error with the fieldbus adapter module. The fieldbus adapter module is an optional add-on that allows the drive to communicate with other devices using industrial communication protocols like Profibus, DeviceNet, or Modbus.
- Check status of fieldbus communication.
- Check settings of parameter groups 50 Fieldbus adapter (FBA), 51 FBA A settings, 52 FBA A data in and 53 FBA A data out.
- Check cable connections.
- Check if communication master is able to communicate.