Forum

Share:
Notifications
Clear all

A8BE ULC overload warning alarm/warning in ABB ACS560 Drive

2 Posts
1 Users
0 Reactions
451 Views
Posts: 18334
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem A8BE ULC overload warning alarm/warning in ABB ACS560 Drive ?

1 Reply
Posts: 18334
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Selected signal has exceeded the user overload curve.

Programmable fault:
37.03 - ULC overload actions

1. Check for any operating conditions increasing the monitored signal (for example, the loading of the motor if the torque or current is being monitored).
2. Check the definition of the load curve (parameter group 37 User load curve).