Forum
Share:
Notifications
Clear all
A8BE ULC overload warning alarm/warning in ABB ACS560 Drive
1 Users
0 Reactions
Admin
Topic starter
(@click2electro)
Member
How can resolve problem A8BE ULC overload warning alarm/warning in ABB ACS560 Drive ?
1 Reply
Admin
Topic starter
(@click2electro)
Member
Cause : Selected signal has exceeded the user overload curve.
Programmable fault:
37.03 - ULC overload actions
1. Check for any operating conditions increasing the monitored signal (for example, the loading of the motor if the torque or current is being monitored).
2. Check the definition of the load curve (parameter group 37 User load curve).
Reply