How can resolve problem 2381 IGBT overload Fault in ABB ACS580 Drive ?

1 Reply
Posts: 19965
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Excessive IGBT junction to case temperature.

This fault protects the IGBT(s) and can be activated by a short circuit in the motor cable.

1. Check motor cable.

2. Remove motor cable then run drive. If fault coming after remove motor cable then drive faulty, if fault not coming then check motor & motor cable.