A2B3 Earth leakage warning in ABB ACS580

2 Posts
1 Users
0 Reactions
1,907 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem A2B3 Earth leakage warning in ABB ACS580 ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Drive has detected load unbalance typically due to earth fault in motor or motor cable.

1. Check for an earth fault in motor or motor cables by measuring the insulation resistances of motor and motor cable.

2. Check Earthing.

3. If problem continue then check drive using multi-meter.

4. Check rectifier & IGBT using multimeter.