How can resolve problem A6E5 AI parametrization warning in ABB ACS580 Drive ?
1 Reply
Oct 21, 2021 7:41 am
Cause : The current/voltage jumper setting of an analog input does not correspond to parameter settings.
1. Adjust either the jumper setting (on the drive control unit) or parameter
12.15/12.25.
Note: Control board reboot (either by cycling the power or through parameter 96.08 - Control board boot) is required to validate any changes in the jumper settings.