How can resolve problem A8BF ULC underload warning in ABB ACS580 Drive ?

1 Reply
Posts: 19965
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Selected signal has fallen below the user underload curve.

Programmable fault:
37.04 -  ULC underload actions

1. Check for any operating conditions decreasing the monitored signal (for example, loss of load if the torque or current is being monitored).
2. Check the definition of the load curve (parameter group 37 User load curve).