ABB ACS580 Drive
2
Posts
1
Users
0
Reactions
541
Views
Oct 21, 2021 8:45 am
How can resolve problem A8BF ULC underload warning in ABB ACS580 Drive ?
1 Reply
Oct 21, 2021 8:45 am
Cause : Selected signal has fallen below the user underload curve.
Programmable fault:
37.04 - ULC underload actions
1. Check for any operating conditions decreasing the monitored signal (for example, loss of load if the torque or current is being monitored).
2. Check the definition of the load curve (parameter group 37 User load curve).