How can resolve problemΒ FF61 ID run Fault in ABB ACS580 Drive ?
1 Reply
Oct 21, 2021 11:26 am
CauseΒ : Motor ID run was not completed successfully.
1. Check the nominal motor values in parameter group 99 Motor data.
2.Β Check that no external control system isΒ connected to the drive.
3.Β Cycle the power to the drive (and itsΒ control unit, if powered separately).
4.Β Check that no operation limits preventΒ the completion of the ID run. RestoreΒ parameters to default settings and tryΒ again.
5.Β Check that the motor shaft is not locked.
6. After this facing any problem then contact us.