ABB ACS800 Drive
1
Posts
1
Users
0
Reactions
213
Views
Jun 19, 2024 5:04 am
Cause : INVERTER CURRENT LIMIT comes when internal inverter current or power limit has been exceeded. This means the current flowing through the inverter that controls the motor is approaching its set limit.
The warning code 2212 in your ABB ACS800 drive indicates a potential issue with the inverter current limit. The inverter is part of the drive that converts DC power from the DC bus into AC power to drive the motor.
- Reduce load or increase ramp time.
- Limit inverter actual power or decrease line- side converter reactive power generation reference value (parameter 95.06 LCU Q PW REF).
- Check Fault Function parameters.