Cause : MOTOR CURRENT LIMIT comes when drive limits motor current according to current limit defined by parameter 20.03 MAXIMUM CURRENT.
The code 2300 in your ABB ACS800 drive indicates a motor current limit warning. This isn't necessarily a fault that will shut down the drive immediately, but it's a notification that the motor current is approaching or exceeding the limit set in the drive parameters.
- Reduce load or increase ramp time.
- Increase parameter 20.03 MAXIMUM CURRENT value.
- Check Fault Function parameters.