Forum

Share:
Notifications
Clear all

2310 OVER CURRENT Fault in ABB ACS800 Drive

2 Posts
1 Users
0 Likes
520 Views
Posts: 14733
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve problem 2310 OVER CURRENT Fault in ABB ACS800 Drive ?

1 Reply
Posts: 14733
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Output current exceeds trip limit.

Check motor load.
Check acceleration time.
Check motor and motor cable (including phasing).
Check encoder cable (including phasing).
Check motor nominal values from group 99
START-UP DATA to confirm that motor model is correct.
Check that there are nopower factor correction or surge absorbers in motor cable.

Reply
Share: