How can resolve problem 4311 THERMISTOR Fault in ABB ACS800 Drive ?
1 Reply
Dec 21, 2021 11:51 am
Cause :Motor temperature is excessive. Motor thermal protection mode selection is TEMP SENSOR.
(programmable Fault Function 30.04...30.05)
Check motor ratings and load.
Check start-up data.
Check thermistor connections to digital input DI6.