4380 warning in ABB ACS800 drive

1 Posts
1 Users
0 Reactions
658 Views
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : TEMPERATURE DIFFERENCE comes when excessive temperature difference between several parallel connected inverter modules. xx (1...12) refers to inverter module number and y refers to phase (U, V, W).

The code 4380 in your ABB ACS800 drive indicates a fault related to an excessive temperature difference between several parallel inverter modules. This signifies a potential overheating issue within the drive that requires attention.

  1. Alarm is indicated when temperature difference is 15°C.
  2. Fault is indicated when temperature difference is 20°C.
  3. Excessive temperature can be caused e.g. by unequal current sharing between parallel connected inverters.
  4. Check cooling fan.
  5. Replace fan.
  6. Check air filters.