Cause : TEMPERATURE DIFFERENCE comes when excessive temperature difference between several parallel connected inverter modules. xx (1...12) refers to inverter module number and y refers to phase (U, V, W).
The code 4380 in your ABB ACS800 drive indicates a fault related to an excessive temperature difference between several parallel inverter modules. This signifies a potential overheating issue within the drive that requires attention.
- Alarm is indicated when temperature difference is 15°C.
- Fault is indicated when temperature difference is 20°C.
- Excessive temperature can be caused e.g. by unequal current sharing between parallel connected inverters.
- Check cooling fan.
- Replace fan.
- Check air filters.