7510 COMM MODULE Warning in ABB ACS800 Drive

2 Posts
1 Users
0 Likes
952 Views
Posts: 14784
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve problem 7510 COMM MODULE Warning in ABB ACS800 Drive ?

1 Reply
Posts: 14784
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Cyclical communication between drive and master is lost.

(programmable Fault Function 30.18, 30.19)

Check status of fieldbus communication.
Check parameter settings:
- group 51 COMM MODULE DATA(for fieldbus adapter)
- group 52 STANDARD MODBUS (for Standard Modbus Link).
Check Fault Function parameters.
Check cable connections.
Check if master can communicate