Forum

Share:
Notifications
Clear all

FF56 fault in ABB ACS800 drive

1 Posts
1 Users
0 Reactions
394 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : MOTOR PHASE FAULT comes when one of motor phases is lost due to fault in motor, motor cable, thermal relay (if used) or internal fault.

The code FF56 in your ABB ACS800 drive indicates a fault related to a missing motor phase. This means the drive is not detecting a signal from one of the three phases that power your motor.

  1. Check motor and motor cable.
  2. Check thermal relay (if used).
  3. Check Fault Function parameters.
  4. Disable this protection.
Share: