ABB ACS800 Drive
1
Posts
1
Users
0
Reactions
193
Views
Jun 19, 2024 5:47 am
Cause : MOTOR TORQUE LIMIT comes when drive limits motor torque according to calculated motor pull-out torque limit and minimum and maximum torque limits defined by parameters 20.13 and 20.14.
- Check parameter 20.13 MIN TORQ SEL and 20.14 MAX TORQ SEL settings.
- Check Fault Function parameters. If LIMIT WORD 1 bit 0 TORQ MOTOR LIM is 1,
- Check motor parameter settings (parameter group 99 START-UP DATA) - ensure that ID run has been completed successfully.