Cause : SPD MATCH FLT comes when speed error at set point is higher than SP DEV LEV (Par. 75.02) or the actual speed change per second during acceleration/ deceleration is less than SPD CHG PER SEC (Par. 75.04) for a time longer than SPD MATCH FLT TD (Par. 75.03) the drive will trip for SPD MATCH FLT.
  1. Check ramp times.
  2. Check Torque and Current limit settings.