How can resolve problem A2005 MOTOR TEMPERATURE alarm in ABB ACS850 Drive ?
Cause : The estimated motor temperature (based on motor thermal model) has exceeded the alarm limit defined by
parameter 31.03 Mot temp1 alarm Limit.
Programmable fault:
31.01 Mot temp1 protection
Allow the motor to cool down and ensure that the motor has attained the correct cooling temperature. Also check the following:
• motor ratings and load
• cooling fan, clean cooling surfaces, etc.
• alarm limit
• motor thermal model settings in parameters 31.09...31.14
Check that the actual number of sensors correspond to the values set by parameter 31.02 Mot temp1 src. Allow the motor to cool down and ensure that the motor has attained the correct cooling temperature.
Also check the following:
• motor ratings and load
• cooling fan, clean cooling surfaces, etc.
• alarm limit