A2005 MOTOR TEMPERATURE alarm in ABB ACS850 Drive

2 Posts
1 Users
0 Reactions
914 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem A2005 MOTOR TEMPERATURE alarm in ABB ACS850 Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : The estimated motor temperature (based on motor thermal model) has exceeded the alarm limit defined by

parameter 31.03 Mot temp1 alarm Limit.

Programmable fault:

31.01 Mot temp1 protection

Allow the motor to cool down and ensure that the motor has attained the correct cooling temperature. Also check the following:
motor ratings and load
cooling fan, clean cooling surfaces, etc.
alarm limit
motor thermal model settings in parameters 31.09...31.14

Check that the actual number of sensors correspond to the values set by parameter 31.02 Mot temp1 src. Allow the motor to cool down and ensure that the motor has attained the correct cooling temperature.
Also check the following:
motor ratings and load
cooling fan, clean cooling surfaces, etc.
alarm limit

 