How can resolve problem A2008 MOTOR ID-RUN alarm in ABB ACS850 Drive ?
1 Reply
Dec 20, 2021 5:14 am
Cause : Motor identification run is on. Motor identification is required.
This alarm belongs to normal start-up procedure. Wait until drive indicates that motor identification is completed.
This alarm belongs to normal start-up procedure.
Select how motor identification should be performed,
parameter 99.13 IDrun mode.
Start identification routines by pressing Start key