How can resolve problem A2030 RESOLVER AUTOTUNE ERR alarm in ABB ACS850 Drive ?
Cause : Resolver autotuning routines, which are automatically started when resolver input is activated for the first time, have failed.
Check cable between resolver and resolver interface module (FEN-21) and order of connector signal wires at both ends of cable.
Check resolver parameter settings. For resolver parameters and information, see parameter group 92 Resolver conf.
Note: Resolver autotuning routines should always be performed after resolver cable connection has been modified. Auto tuning routines can be activated by setting parameter 92.02 Exc signal ampl or 92.03 Exc signal freq, and then setting parameter 90.10 Enc par refresh to Configure.