Forum
Share:
Notifications
Clear all
A2039 EARTH FAULT alarm in ABB ACS850 Drive
1 Users
0 Reactions
Admin
Topic starter
(@click2electro)
Member
How can resolve problem A2039 EARTH FAULT alarm in ABB ACS850 Drive ?
1 Reply
Admin
Topic starter
(@click2electro)
Member
Cause : Drive has detected load unbalance typically due to earth fault in motor or motor cable.
Programmable fault:
30.05 Earth fault
Check there are no power factor correction capacitors or surge absorbers in motor cable.
Check for an earth fault in motor or motor cables by measuring the insulation resistances of motor and motor cable