F0045 FIELDBUS COMM Fault in ABB ACS850 Drive

2 Posts
1 Users
0 Likes
348 Views
Posts: 14784
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve problem F0045 FIELDBUS COMM Fault in ABB ACS850 Drive ?

1 Reply
Posts: 14784
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Cyclical communication between drive and fieldbus adapter module or between PLC and fieldbus adapter module is lost.

Check status of fieldbus communication.
See the appropriate User’s Manual of
fieldbus adapter module.
Check settings of parameter group 50
Fieldbus.
Check cable connections.
Check if communication master is able to
communicate.