Cause : Overcurrent comes when output current has exceeded internal fault limit or the current flowing through the drive has exceeded its specified limit.
A 2E00 fault code in your ABB ACS880 drive signifies an overcurrent condition. This means the current flowing to the motor has exceeded the safe operating limits for an extended period.
- Check supply voltage.
- Check that there are no power factor correction capacitors or surge absorbers in supply cable.
- Check motor load and acceleration times.
- Check power semiconductors (IGBTs) and current transducers.