Cause : LSU charging busbar fault comes when the DC voltage rise in 10 ms is not acceptable during charging. The level is below the value set in parameter 120.26 Maximum dU/dt, but DC voltage has not reached the level set in parameter 120.25 MCB closing level.
- Check the connections of the DC capacitors in the power modules and parameters 120.25 MCB closing level and 120.26 Maximum dU/dt.
- Check that the input voltage is stable during start.