ABB ACS880 Drive
1
Posts
1
Users
0
Reactions
489
Views
Jun 11, 2024 8:39 am
Cause : Reduced run comes when number of inverter modules detected does not match the value of parameter 95.13 Reduced run mode.
- Check that the value of 95.13 Reduced run mode corresponds to the number of inverter modules present.
- Check that the modules present are powered from the DC bus and connected by fiber optic cables to the BCU control unit.
- If all modules of the inverter unit are in fact available (eg. maintenance work has been completed), check that parameter 95.13 Reduced run mode is set to 0 (reduced run function disabled).