Forum

Share:
Notifications
Clear all

5E0D fault in ABB ACS880 drive

1 Posts
1 Users
0 Reactions
191 Views
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : PU communication configuration comes when version check cannot find a matching power unit FPGA logic, or number of connected power modules differs from specified.

Check the auxiliary code (format ZZZY YYXX). “XX” specifies the configuration error cause

  • 1: Found BAMU 1 configured in wrong channel,
  • 2: Found BAMU 2 configured in wrong channel,
  • 3: Found PUs configured in wrong channels,
  • 4: Found PU configured in wrong channel,
  • 5: Found too many PUs.
  • Check settings of parameters 195.31 Parallel connection rating id and 191.30 BAMU 1 channel.
Share: