Cause : LSU charge failed comes when the supply unit was not ready (ie. the main contactor/breaker could not be closed) within expected time.
- Check that communication to the supply unit has been activated by 95.20 HW options word 1.
- Check that the supply unit is enabled, allowed to start, and can be controlled by the inverter unit (eg. not in local control mode).