Cause : FBA A communication comes when cyclical communication between the supply unit and fieldbus adapter module A or between PLC and fieldbus adapter module A is lost.

Programmable fault: 150.02 FBA A comm loss function

  1. Check status of fieldbus communication.
  2. See user documentation of fieldbus interface.
  3. Check settings of parameter groups 150 FBA, 151 FBA A settings, 152 FBA A data in and 153 FBA A data out.
  4. Check cable connections.
  5. Check if communication master is able to communicate.