ABB ACS880 Drive
1
Posts
1
Users
0
Reactions
435
Views
Jun 12, 2024 6:22 am
Cause : Auxiliary fan not running comes when an auxiliary cooling fan (connected to the fan connectors on the control unit) is stuck or disconnected.
- The auxiliary code identifies the fan (1: Auxiliary fan 1, 2: Auxiliary fan 2).
- Check that the auxiliary fan supervision selection in parameter 95.21 HW options word 2 matches the hardware.
- Make sure the front cover of the drive module is in place and tightened. Check auxiliary fan(s) and connection(s).
- Replace faulty fan.