Cause : ULC configuration comes when user load curve configuration error due to speed points inconsistent, frequency points inconsistent, underload point above overload point or overload point below underload point.
- Check that each speed point (parameters 37.11…37.15) has a higher value than the previous point.
- Check that each frequency point (37.16…37.20) has a higher value than the previous point.
- Check that each overload point (37.31…37.35) has a higher value than the corresponding underload point (37.21…37.25).
- Check that each overload point (37.31…37.35) has a higher value than the corresponding underload point (37.21…37.25).