"ABB ACS880 Fault Codes list" indicate an error occur in drive due to internal hardware problem or parameter issue. With the help of these error code you can easily identify and correct the issue in drive.

ABB ACS880 Fault Codes list and their solutions:

2281 Calibration - Measured offset of output phase current measurement or difference between output phase U2 and W2 current measurement is too great (the values are updated during current calibration).

2310 Overcurrent - Output current has exceeded internal fault limit.

2330 Earth leakage - Drive has detected load unbalance typically due to earth fault in motor or motor cable.

2340 Short circuit- Short-circuit in motor cable(s) or motor.

2381 IGBT overload - Excessive IGBT junction to case temperature. This fault protects the IGBT(s) and can be activated by a short circuit in the motor cable.

3130 Input phase loss - Intermediate circuit DC voltage is oscillating due to missing input power line phase or blown fuse.

3180 Charge relay lost - No acknowledgement received from charge relay.

3181 Cross connection - Incorrect input power and motor cable connection (i.e. input power cable is connected to drive motor connection).

3210 DC link overvoltage  - Excessive intermediate circuit DC voltage.

3220 DC link undervoltage - Intermediate circuit DC voltage is not sufficient because of a missing supply phase, blown fuse or fault in the rectifier bridge.

3280 Standby timeout- Automatic restart failed.

3291 DC voltage difference - Difference in DC voltages between parallel-connected inverter modules.

3381 Output phase loss - Motor circuit fault due to missing motor connection (all three phases are not connected).

3385 Autophasing - Autophasing routine.

4210 IGBT overtemperature - Estimated drive IGBT temperature is excessive.

4290 Cooling - Drive module temperature is excessive.

4310 Excess temperature - Power unit module temperature is excessive.

4380 Excess temperature difference - High temperature difference between the IGBTs of different phases.

42F1 IGBT temperature - Drive IGBT temperature is excessive.

4981 External temperature - Measured temperature 1 or 2 has exceeded fault limit.

5080 Fan - Cooling fan stuck or disconnected.

5090 STO hardware failure - Safe torque off hardware failure.

5091 Safe torque off - Safe torque off function is active, i.e. safety circuit signal(s) connected to connector XSTO is broken during start or run, or while drive is stopped and parameter 31.22 STO diagnostics is set to Fault.

5092 PU logic error - Power unit memory has cleared.

5093 Rating ID mismatch - The hardware of the drive does not match the information stored in the memory unit. This may occur eg. after a firmware update or memory unit replacement.

5681 PU communication - Communication errors detected between the drive control unit and the power unit.

5682 Power unit lost - Connection between the drive control unit and the power unit is lost.

5690 PU communication internal - Internal communication error.

5691 Measurement circuit ADC - Measurement circuit fault.

5692 PU board powerfail - Power unit power supply failure.

5693 Measurement circuit DFF - Measurement circuit fault.

5694 PU communication configuration - Version check cannot find a matching power unit FPGA logic.

5696 PU state feedback - State feedback from output phases does not match control signals.

5697 Charging feedback - Charging feedback signal missing.

5698 Unknown power unit fault - Unidentified power unit logic fault.

 