Forum

Share:
Notifications
Clear all

AE27 fault in ABB ACS880 drive

1 Posts
1 Users
0 Reactions
165 Views
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : AI parameterization comes when the current/voltage jumper setting of an analog input does not correspond to parameter settings.

Adjust either the jumper setting (on the control unit) or parameter 112.15/112.25.

Note: Control board reboot (either by cycling the power or through parameter 196.08 Control board boot) is required to validate any changes in the jumper settings.

Share: