ABB ACS880 Drive
1
Posts
1
Users
0
Reactions
165
Views
Jun 14, 2024 12:38 pm
Cause : AI parameterization comes when the current/voltage jumper setting of an analog input does not correspond to parameter settings.
Adjust either the jumper setting (on the control unit) or parameter 112.15/112.25.
Note: Control board reboot (either by cycling the power or through parameter 196.08 Control board boot) is required to validate any changes in the jumper settings.