Forum

Share:
Notifications
Clear all

AE56 fault in ABB ACS880 drive

1 Posts
1 Users
0 Reactions
160 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : INU-LSU comm loss comes when DDCS (fiber optic) communication between converters (for example, the inverter unit and the supply unit) is lost.

  1. Check settings of parameter group 160 DDCS communication.
  2. Check the corresponding settings in the control program of the other converter.
  3. Check the cable connections. If necessary, replace the cables.
Share: