Cause : INU-LSU comm loss comes when DDCS (fiber optic) communication between converters (for example, the inverter unit and the supply unit) is lost.
  1. Check settings of parameter group 160 DDCS communication.
  2. Check the corresponding settings in the control program of the other converter.
  3. Check the cable connections. If necessary, replace the cables.