FE06 fault in ABB ACS880 drive

1 Posts
1 Users
0 Reactions
250 Views
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : MF communication loss comes when master/follower communication is lost. On the FDCO module (if present), check that the DDCS link switch is not set to 0 (OFF)

  1. Check the auxiliary code.
  2. The code indicates which node address (defined by parameter 160.02 in each supply unit) on the master/follower link is affected.
  3. Check settings of parameter group 160 DDCS communication.
  4. Check the cable connections.
  5. If necessary, replace the cables.