Forum
Share:
Notifications
Clear all
A2002 BRAKE NOT OPEN alarm in ABB ACSM1 Drive
1 Users
0 Reactions
Admin
Topic starter
(@click2electro)
Member
How can resolve problem A2002 BRAKE NOT OPEN alarm in ABB ACSM1 Drive ?
Topic Tags
1 Reply
Admin
Topic starter
(@click2electro)
Member
Cause : Mechanical brake control alarm. Alarm is activated, eg, if brake acknowledgement is not as expected during brake opening.
Programmable fault: 35.09 BRAKE FAULT FUNCTION
Check mechanical brake connection.
Check mechanical brake settings, parameters
35.01...35.08.
To determine whether problem is with
acknowledgement signal or brake: Check if
brake is closed or open
Reply